Sizing a capacitor for power factor correction

Question EEE-105

A single-phase load draws 10 kW at 0.8 power factor lagging from a 230 V, 50 Hz supply. What capacitance must be connected in parallel to raise the power factor to 0.95 lagging? By how much does the supply current fall?

Show hints

The capacitor supplies the difference in reactive power: Q_c = P(tan φ₁ − tan φ₂).

Show the explanation

Worked answer.

The real power P = 10 kW does not change when a capacitor is added. Only the reactive power drawn from the supply changes.

Step 1: Reactive power before correction. cos φ₁ = 0.8, so sin φ₁ = 0.6 and tan φ₁ = 0.75.
Q₁ = P tan φ₁ = 10 × 0.75 = 7.5 kVAR.

Step 2: Reactive power after correction. cos φ₂ = 0.95, so φ₂ ≈ 18.19° and tan φ₂ ≈ 0.3287.
Q₂ = 10 × 0.3287 ≈ 3.287 kVAR.

Step 3: Capacitor kVAR. Q_c = Q₁ − Q₂ = 7.5 − 3.287 ≈ 4.21 kVAR.

Step 4: Capacitance. For a capacitor across voltage V, Q_c = V² ωC, so
C = Q_c / (2πf V²) = 4213 / (2π × 50 × 230²) = 4213 / (314.16 × 52,900) ≈ 2.535 × 10⁻⁴ F ≈ 254 µF.

Step 5: Supply current. Before: I₁ = P / (V cos φ₁) = 10,000 / (230 × 0.8) ≈ 54.3 A. After: I₂ = 10,000 / (230 × 0.95) ≈ 45.8 A. The current falls by about 8.6 A (about 16%).

Check. Apparent power after correction is √(10² + 3.287²) ≈ 10.53 kVA, and 10.53 kVA / 230 V ≈ 45.8 A, which matches Step 5.

Common mistake. Using kVA instead of kW as the base for tan φ, or forgetting that P stays constant. Another frequent slip is using ω = 50 instead of 2π × 50.

Likely follow-up. "Why not correct all the way to unity?" The last few percent need disproportionately more kVAR, and over-correction at light load can make the power factor leading and raise the voltage. Utilities typically target around 0.95 to 0.99.

Original UniCircle question. Last reviewed 28 Oct 2026.